Flashing over speed red led

Generac, Guardian, Honeywell, Siemens, Centurion, Watchdog, Bryant, Olympian & Carrier Liquid Cooled Home Standby & Commercial generator troubleshooting and repair questions
Chris
Site Admin
Site Admin
Posts: 236
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Thu Mar 14, 2019 6:01 pm

Just swap the hose, which should be the same directions as the owner's manual as well. Make sure though... Normally the outside of the body of the regulator will have the jet sizes marked in marker on there. LP has a higher BTU content, so it requires a smaller jet size.
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
g&bporcelain
New Member
New Member
Posts: 22
Joined: Mon Feb 11, 2019 4:44 pm

Fri Mar 15, 2019 5:23 pm

changed hose connector to the smaller jet side . its not surging but is popping out the exhaust like a car sound with water in the gas. i checked plugs, dist cap ,rotor and firing order all look good. any suggestions?
Chris
Site Admin
Site Admin
Posts: 236
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Fri Mar 15, 2019 8:27 pm

What is the fuel pressure like?
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
g&bporcelain
New Member
New Member
Posts: 22
Joined: Mon Feb 11, 2019 4:44 pm

Mon Mar 18, 2019 4:38 pm

not sure the last tech who worked on it adjusted the fuel regulator to get the smoothest run. could i adjust it in or out while its running to see if that helps if so which direction and how many turns to get closer to the sweet spot
g&bporcelain
New Member
New Member
Posts: 22
Joined: Mon Feb 11, 2019 4:44 pm

Mon Mar 18, 2019 4:39 pm

he adjusted it before i connected hose to smaller jet
Chris
Site Admin
Site Admin
Posts: 236
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Mon Mar 18, 2019 6:01 pm

That regulator is not adjustable, the jet just gets installed and put back together.
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
g&bporcelain
New Member
New Member
Posts: 22
Joined: Mon Feb 11, 2019 4:44 pm

Mon Mar 18, 2019 9:20 pm

im talking about the regulator the gas co put in line between the lp tank and the generator
Chris
Site Admin
Site Admin
Posts: 236
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Mon Mar 18, 2019 10:57 pm

You need a manometer to measure gas pressure. Don't just adjust it around without knowing where it really is. The LP company would probably come out and test it for you.
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
g&bporcelain
New Member
New Member
Posts: 22
Joined: Mon Feb 11, 2019 4:44 pm

Mon Mar 25, 2019 6:56 pm

put a manometer and adjusted lp regulator under load around 10 in water column ran best. is it normal for a burst of smoke to come out just for about 2 seconds when engine fires up
is this a characteristic of lp for fuel?
78buckshot
Verified Dealer
Verified Dealer
Posts: 43
Joined: Mon Nov 12, 2018 9:45 am
Location: Stockbridge/Chelsea, Michigan

Mon Mar 25, 2019 7:38 pm

The color of the smoke helps tell the story. White or blue/white smoke is oil burning in the cylinder or exhaust, black smoke is excess fuel.