Dek 5000 no power

Portable standby generator troubleshooting and repair questions. (Gasoline, diesel, propane, natural gas)
Post Reply
hiltbuck
New Member
New Member
Posts: 1
Joined: Thu Oct 10, 2019 7:03 pm

Dek5000, brushless generator, no power, tested voltage L1-L2 = 2v , R1-R2 = 2v, between capacitor leads = 5.2v. Replaced capacitor, half moon style, no change. Had capacitors tested = both good. Tried reverse drill trick = no change, but drill was very difficult to spin backwards. Charged capacitor with 110v = no change. Connected 110v to capacitor while running = generator produced 60v, but only while 110v leads were connected.
Any ideas or suggestions?
ChrisMills
New Member
New Member
Posts: 6
Joined: Sat Nov 30, 2019 6:39 am

It's an old thread but w/ no response.

You might test the L1 & l2 windings for resistance in ohms. They're probably not broken if you're getting voltage but you never know. Next would be to check the resistance of L1 & L2 to ground. That should read infinite resistance.

It seems a good possibility that the exciter coil windings are damaged if so equipped.