Fri Aug 02, 2019 8:42 pm

Hope someone might have a thought before I purchase a new board. I have confirmed 240vac at the generator and I suspect the board or component had gotten fried. This is an 11kw air cooled. I am unsure where exactly the surge got onto my lines but a few breakers in the house did trip. I was not home but I do not think the generator tried to run, it was in setup mode like when I originally installed. Date data, etc.. was not retained. If I put it in auto after the delay it starts, I have not let it run long enough to see if the transfer switches or not.

Thanks!
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Fri Aug 02, 2019 8:48 pm

Check the voltage with some type of load and not just a digital meter. A Wiggy style meter will apply a small load to the lines which may reveal a bad fuse that a digital won't catch.

What's the serial number on the unit? I assume this is an Evo 1.0 controller?
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Tom G
New Member
New Member
Posts: 3
Joined: Fri Aug 02, 2019 8:35 pm

Fri Aug 02, 2019 9:06 pm

Chris wrote:
Fri Aug 02, 2019 8:48 pm
Check the voltage with some type of load and not just a digital meter. A Wiggy style meter will apply a small load to the lines which may reveal a bad fuse that a digital won't catch.

What's the serial number on the unit? I assume this is an Evo 1.0 controller?
Thanks Chris,

I was pretty certain the voltage was the real deal but I threw a starter on the terminals at the generator for kicks and giggles.

SN 3000060380
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Fri Aug 02, 2019 10:21 pm

A starter?? On 240v? :shocked:
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Fri Aug 02, 2019 10:25 pm

That is an Evo 1.0 unit, so this would be the controller for it: https://shop.gentekpower.com/products/g ... trol-panel
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Tom G
New Member
New Member
Posts: 3
Joined: Fri Aug 02, 2019 8:35 pm

Sat Aug 03, 2019 8:12 am

Chris wrote:
Fri Aug 02, 2019 10:21 pm
A starter?? On 240v? :shocked:
LOL, a 240vac contactor for fans/heaters/etc.., pretty common in hvac split systems, just grabbed what was on the truck.
Thanks, I saw the part on your site, I assume then that would be your next step, will get it ordered?
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Sat Aug 03, 2019 8:27 am

Haha, sorry I didn't realize that's what you meant! :ahh: I would say that's the logical next step. If you have power all the way up to the controller and the controller isn't detecting it, that makes me think the surge/strike probably smoked the PCB inside :sad:
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Post Reply