Blows fuse

Generac, Guardian, Honeywell, Siemens, Centurion, Watchdog, Bryant, & Carrier Air Cooled Home Standby generator troubleshooting and repair questions
Post Reply
kyf301
New Member
New Member
Posts: 12
Joined: Thu Jul 11, 2019 2:51 pm

Thu Jul 11, 2019 4:41 pm

Mo.# 04079-3 10 kw. Ser. 3513884 Nat. Gas - I have test gear. All these problems are with no load. Runs for 5 minuets and I shut it down.. Will not restart because of blown fuse. Replace fuse and starts right up, runs for 30 seconds and blows fuse. With meter I find wire 194 goes to ground. Wait a few minuets and then 194 is open. Doesn't make any sense. Need help.
Chris
Site Admin
Site Admin
Posts: 790
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Thu Jul 11, 2019 4:53 pm

I would advise removing the 23 and 194 wires from the terminal block and test it like that. It could be a short somewhere in the wiring between the transfer switch and the generator. A high resistance fault like a rubbed through wire may be causing the issue.
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
kyf301
New Member
New Member
Posts: 12
Joined: Thu Jul 11, 2019 2:51 pm

Fri Jul 12, 2019 11:38 am

The unit runs fine with the 194 and 23 wire disconnected from terminal block. I'll look for a grounded wire as you suggested.
78buckshot
Verified Dealer
Verified Dealer
Posts: 96
Joined: Mon Nov 12, 2018 9:45 am
Location: Stockbridge/Chelsea, Michigan

Fri Jul 12, 2019 8:07 pm

I have seen condensation form inside metal conduit, then cause a short in the control wires if they had been skinned during installation.
kyf301
New Member
New Member
Posts: 12
Joined: Thu Jul 11, 2019 2:51 pm

Mon Jul 15, 2019 3:46 pm

I never found a short or anything. Took all the wires out of the flexible conduit and found nothing. Replaced the 23 and 19 wires back to terminal block and ran the unit and it ran fine. I don't understand how it would run now without really changing anything. I haven't ran it under load yet, but will do soon.
Chris
Site Admin
Site Admin
Posts: 790
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Mon Jul 15, 2019 4:35 pm

I bet somewhere there's a very tiny bad spot in a wire. When the short takes some time to blow a fuse, that's a sure sign there is weak insulation somewhere. If it were touching metal it would blow instantly. Hopefully that corrects the problems!
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
kyf301
New Member
New Member
Posts: 12
Joined: Thu Jul 11, 2019 2:51 pm

Mon Jul 22, 2019 11:11 am

Haven't found anything like that yet. Still looking.
kyf301
New Member
New Member
Posts: 12
Joined: Thu Jul 11, 2019 2:51 pm

Sat Aug 24, 2019 2:47 pm

My unit no longer blows fuses. It seems to be fine. Thanks for the help.
UPS
New Member
New Member
Posts: 19
Joined: Thu Dec 06, 2018 12:40 pm

Sat Aug 24, 2019 7:15 pm

If there was a bad spot in the insulation on a wire, and it was hitting ground, you may have fixed it by moving the wires while troubleshooting.
Post Reply