Battery Not holding a Charge Generac Model G0070431 22KW

Generac, Guardian, Honeywell, Siemens, Centurion, Watchdog, Bryant, & Carrier Air Cooled Home Standby generator troubleshooting and repair questions
Post Reply
LPolitewicz
New Member
New Member
Posts: 4
Joined: Fri May 10, 2019 11:22 am

Fri May 10, 2019 11:26 am

My battery died recently on my 22KW air cooled. I replaced the battery with the 26R and 2 days later I am getting a LOW BATTERY alarm on the display. Checked the voltage and it is at 10 V. Where is the charging unit? And how could I troubleshoot it ?
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Fri May 10, 2019 11:40 am

The charger is built into the controller on this unit. You should have 120V input on the T1 wire which is power for the charger internally.

Does the display also say Charger Missing AC?
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
LPolitewicz
New Member
New Member
Posts: 4
Joined: Fri May 10, 2019 11:22 am

Fri May 10, 2019 12:08 pm

Yes it said missing AC. I have 120 V on the T1 wire. Now it says low battery.
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Fri May 10, 2019 2:31 pm

If the screen said Charger Missing AC, that means that the battery charger inside the controller isn't seeing 120V power for some reason... I would check your connections at the generator and make SURE that you actually have 120V power on the T1 wire. Can you post a couple of pictures of the install?
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
LPolitewicz
New Member
New Member
Posts: 4
Joined: Fri May 10, 2019 11:22 am

Sat May 11, 2019 4:51 pm

Chris. I found the terminal block that the T1 wire was connected to in the unit was not gripping the wire properly. I was able to pull the blue wire out without pressing down on the release +. I tried several times to land the wire correctly but the block wouldn't hold it in place. So I removed both the blue and the T1 wire and connected using a solderless yellow push in connector. The Missing AC fault is now gone. However I still have the low battery. I am going to see if it charges. If not I will just replace the battery.

One other question how do I get the firmware update for my controller. I cannot find it on the generac website.
78buckshot
Verified Dealer
Verified Dealer
Posts: 93
Joined: Mon Nov 12, 2018 9:45 am
Location: Stockbridge/Chelsea, Michigan

Sat May 11, 2019 7:51 pm

The on-board charger is not designed to bring a dead battery back, you may damage the charger. I would remove the battery and charge it with a stand-alone charger.
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Sat May 11, 2019 10:58 pm

Like Buckshot said, I'd charge the battery (removed from the gen) and then try it.

As far as firmware goes, that's really a dealer only item. I'd contact your local dealer and see what they would charge to make a visit and install. Takes about 30 seconds... I personally like version 1.17 best as 1.18 and 1.20 are designed for the Auxiliary Shutdown kits and if not installed could possibly cause a false trip.
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
LPolitewicz
New Member
New Member
Posts: 4
Joined: Fri May 10, 2019 11:22 am

Tue May 14, 2019 8:50 am

Ok I replaced the battery yesterday and now I am getting a charger warning on the LCD. Is the charging unit on the controller the issue? Could you get me a part number? Serial # 3002664643
Chris
Site Admin
Site Admin
Posts: 601
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Tue May 14, 2019 9:38 am

This is the controller that fits your generator. https://shop.gentekpower.com/products/g ... trol-panel

You should be able to monitor battery voltage pretty easily with a meter. Check the battery voltage before cranking the gen, should be around 13.5V or so, then crank the gen and it should drop to around 11.8 or so, then you should be able to watch it slowly climb back up to the 13.5.

If the battery is not charging, the controller will slowly kill the battery.
Generac tech for over 12 years. I'm here to help!