Post a picture of the hose setup so we can see what's going on. I can't imaging that anything is wrong with how it's routed if it ever worked before, and that primer solenoid looks like it's piped right into the tee.
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Rob_marek83
Contributor
Contributor
Posts: 25
Joined: Sun Oct 25, 2020 7:29 pm

Will do tomorrow.

I think I figured out my problem to fuel pressure. Need to call gas company and see if I can squeeze another 1.5 in of water Column out of my regulator
Rob_marek83
Contributor
Contributor
Posts: 25
Joined: Sun Oct 25, 2020 7:29 pm

Here you go.
Attachments
AEC611CC-EAC8-4387-8D5F-C2E3CE033155.jpeg
AEC611CC-EAC8-4387-8D5F-C2E3CE033155.jpeg (200.14 KiB) Viewed 79 times
1575B271-DA70-4FB6-B9DB-18E6C95F1A29.jpeg
1575B271-DA70-4FB6-B9DB-18E6C95F1A29.jpeg (195.01 KiB) Viewed 79 times
38F9AB44-5557-4C5C-BF56-7BBFAB0EDC43.jpeg
38F9AB44-5557-4C5C-BF56-7BBFAB0EDC43.jpeg (203.98 KiB) Viewed 79 times
58545C86-D4B5-4D0F-9A48-08228E0446B6.jpeg
58545C86-D4B5-4D0F-9A48-08228E0446B6.jpeg (197.28 KiB) Viewed 79 times
B383A152-4B30-4D04-9504-280241BE85DA.jpeg
B383A152-4B30-4D04-9504-280241BE85DA.jpeg (193.12 KiB) Viewed 79 times
Chris
Site Admin
Site Admin
Posts: 3256
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

That setup looks totally normal to me. I don't see anything altered or anything like that. It could be that the fuel regulator is giving you some trouble. There are 5 small holes on the diaphragm cover. If you take a small allen wrench and GENTLY push in while the unit is cranking, does it fire up? Basically what you're doing it adding fuel to the mix.
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Rob_marek83
Contributor
Contributor
Posts: 25
Joined: Sun Oct 25, 2020 7:29 pm

Where is the diaphragm cover? The silver round thing? Sorry for the noob question lol
Rob_marek83
Contributor
Contributor
Posts: 25
Joined: Sun Oct 25, 2020 7:29 pm

So I found what you were talking about and if I do push in, it almost wants to start. Does that tell you I have a fuel pressure problem?

When it is not trying to start the diaphragm is pretty loose. And only after a few seconds of cranking do you feel it push back on the Allen wrench and I need to apply some force.
Post Reply