Generac 17kw unit surging

Posted: Tue Jun 30, 2020 1:58 pm
by aparker
Good afternoon,

I have a 17kw generac unit that is surging. I've replaced the main mother board and the motor stepper assembly but there is no change. What else could be causing this surging? Thank you for your help!

Re: Generac 17kw unit surging

Posted: Tue Jun 30, 2020 4:44 pm
by Chris
Can you post some info about the generator? Model/serial would be the most helpful.

Re: Generac 17kw unit surging

Posted: Thu Jul 09, 2020 1:06 pm
by aparker
Thank you for the reply! The generator is a Guardian 17kw unit. Model number is 0055230, and the serial number is 5132203.

Re: Generac 17kw unit surging

Posted: Thu Jul 09, 2020 11:57 pm
by Chris
These older units weren't really known for surging, so that makes me think fuel problem, or possibly a bad ignition coil sending a weird RPM signal to the controller.

Can you test the fuel pressure?