Hi temp fault

Generac, Guardian, Honeywell, Siemens, Centurion, Watchdog, Bryant, & Carrier Air Cooled Home Standby generator troubleshooting and repair questions
Post Reply
Rfkasica
New Member
New Member
Posts: 1
Joined: Fri Sep 25, 2020 3:58 pm

Have Generac 8kw model 0062510. 860 hrs on generator. 4 yrs old. Got hi temp fault. Checked for airflow- nothing blocked, checked/replaced sensor. Wiring to sensor good. Have not checked wiring to electronics (Have no schematic). Start cold generator ( off for several hours here in Alaska), fault alarm comes on after about 10 seconds. Removed and replaced fuse. Same results, (did not reset fault). Is there a way to reset fault?
grsthegreat
Generator Guru
Generator Guru
Posts: 341
Joined: Mon Apr 20, 2020 5:59 pm

DE4C42B6-B214-4A4F-93A2-96B7D9062018.png
DE4C42B6-B214-4A4F-93A2-96B7D9062018.png (207.56 KiB) Viewed 56 times
Did you get an error code 1400? You can reset alarm code by putting generator in STOP mode and pressing enter button 2 times.

Are you sure you replaced the proper temp sender. I have enclosed the testing procedure.

Going just by model number, the thermostat part should be #094090. But to be more exact you need to post serial number. Generac lists all parts against serial numbers. The same model line can have different parts over the years.