When transferring back to utility power, transfer switch Generac 4945-1 200 amp main breaker trips (when several central AC units are operating from generator power). In trying to replace main utility breaker with identical Siemens unit, cannot get old breaker off of blades to remove.
Have removed single screw in center top of breaker that holds top of breaker onto ATS back panel. Pulling on top of breaker allows the breaker to pull out about 0.5” but then stops and further pressure tends to pull blade mounting from back panel of enclosure.
Any ideas on why breaker is stuck and how to extract will be appreciated.
Chris
Site Admin
Site Admin
Posts: 5998
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Can you post some images of the switch and breaker?
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Rawley
New Member
New Member
Posts: 4
Joined: Tue Aug 02, 2022 3:16 pm

Sorry for the delay. I was away from the site.
Attachments
67D9824B-B9A8-44AB-BF37-C1EB7FDF9C6B.jpeg
67D9824B-B9A8-44AB-BF37-C1EB7FDF9C6B.jpeg (109.34 KiB) Viewed 301 times
03EF1640-D97F-423C-A773-56B8BF2D965C.jpeg
03EF1640-D97F-423C-A773-56B8BF2D965C.jpeg (152.43 KiB) Viewed 301 times
F3B04EDB-F5A5-4F96-BB54-D4B933AEEEBD.jpeg
F3B04EDB-F5A5-4F96-BB54-D4B933AEEEBD.jpeg (140.02 KiB) Viewed 301 times
A07BA814-A400-4A53-9721-4FA281F3382D.jpeg
A07BA814-A400-4A53-9721-4FA281F3382D.jpeg (222.44 KiB) Viewed 301 times
grsthegreat
Generator Jedi Master
Generator Jedi Master
Posts: 2227
Joined: Mon Apr 20, 2020 5:59 pm

Theoretically if you .remove the small screw in face of breaker, it will pop right off. Im not sure why it isnt pulling off of tabs. In house panels they pull off easily. This looks like the same breaker as used in standard siemens 200 and 400 amp panels.
C26869B8-3588-4369-8E63-F1185BB8D315.png
C26869B8-3588-4369-8E63-F1185BB8D315.png (347.65 KiB) Viewed 300 times
Rawley
New Member
New Member
Posts: 4
Joined: Tue Aug 02, 2022 3:16 pm

As I indicated, the retaining screw was removed prior to trying to remove the breaker.
Thanks for your reply and help. Any other thoughts would be appreciated.
Chris
Site Admin
Site Admin
Posts: 5998
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Are the buss bars that connect to the contactor holding you up? It also makes me wonder if there was arcing behind the breaker which is also why it's tripping. If the tabs have been damaged, they may be hanging up or something?
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Rawley
New Member
New Member
Posts: 4
Joined: Tue Aug 02, 2022 3:16 pm

That is my thought that the blades have been damaged by internal arcing but don’t have a way to verify or test the theory. I guess my question is has anyone experienced this in another installation? Any suggestions will be appreciated.
grsthegreat
Generator Jedi Master
Generator Jedi Master
Posts: 2227
Joined: Mon Apr 20, 2020 5:59 pm

In 35 years of electrical ive had to replace many main breakers, but ive never had an issue removing old breaker.

However, i have never had to replace a generac main breaker. Sorry cant help you with that.
Chris
Site Admin
Site Admin
Posts: 5998
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

Generac tech for over 12 years. I'm here to help!