I am also VERY pleased with the Hyper Sure Start that i just recently placed on my 4 ton AC compressor. I used to see a micro burst of up to 97 amp load when the compressor kicked on. today i saw 22 amp. I ran this test while using generator to power my house. The generator didnt even burp.
Chris
Site Admin
Site Admin
Posts: 3824
Joined: Sat Aug 04, 2018 8:46 pm
Location: Clawson, MI
Contact:

It's honestly like magic! :lmao:
Generac tech for over 12 years. I'm here to help!
"The only source of knowledge is experience" -Albert Einstein
Looking for Generac parts? Gentek Power offers the full line of Generac replacement parts! Shop Gentek Power Generac Parts
A list of my favorite Generator & Electrical Tools! https://www.amazon.com/shop/gentek_power
Half Vast
New Member
New Member
Posts: 9
Joined: Sun Feb 02, 2020 8:44 am

Agree 100% with this. Recently purchased one (thanks Chris!) from the online shop here to add to my 5 ton Goodman outdoor unit. My 22kW Honeywell would bog down and start shedding loads when this AC beast kicked in. I checked inrush current and measured 117A peak inrush. Did that for a few starts for consistent readings. Next, installed the SureStart and let it do its things for a week (says it requires several starts to fine tune itself). Checked the current today and the inrush has been reduced to 70A peak inrush. Haven't done a full load generator test yet (planned for the weekend) to see how the generator acts. Once I do, I'll update this.

Thanks again Chris!

UPDATE 8/24/2020

Ran the generator with full load yesterday to test the effect of the SureStart. Once the generator was warmed up I placed a cooling demand on the 5 ton unit. The generator didn't even blip. Good product and glad I got it here.
Last edited by Half Vast on Fri Aug 28, 2020 4:51 am, edited 1 time in total.
jakespeed
New Member
New Member
Posts: 8
Joined: Tue Jul 21, 2020 1:43 pm

tested ats for the first time today with surestart on a 4ton ruud. there was no change in the sound of the generator when i turned on the hvac. inrush load of hvac dropped to 24amps. now i need to wire the thermostat into the ats
brnmcc01
Top Contributor
Top Contributor
Posts: 81
Joined: Mon Apr 27, 2020 9:53 pm
Location: Bloomington, IN

I've also had one on my 2ton A/C unit for 2+ years now. Rated LRA on this unit is 55, I have a 9kw generator that was able to start it without one, but it bogged it down a bit. With the Surestart, inrush is only about 22 amps, and is much easier to start and run with surestart installed! from June 2019. Very happy with it.