I cannot start my 4000 watt Generac generator. There is no spark. The oil level is full. Is there a way of checking out the run start switch? Can it be by passed?

Thank you

RV
grsthegreat
Generator Jedi Master
Generator Jedi Master
Posts: 1527
Joined: Mon Apr 20, 2020 5:59 pm

The switch wont have anything to do with not producing spark. Is the unit turning over when you press start switch?
rvs57lin
New Member
New Member
Posts: 6
Joined: Mon Nov 22, 2021 10:41 am

My 4000 generac does not have an electric start. My question was is there a way to by pass the stop-run switch. I am sure that the stop-run switch will prevent a spark to the spark plug if it is in the stop position or stuck in the stop position. I would just like to by pass it if I can to see if I get a spark

Thank you

RV
rvs57lin
New Member
New Member
Posts: 6
Joined: Mon Nov 22, 2021 10:41 am

I did say in my first post that I wanted to know if I could by pass the run- start switch, my mistake here i should have said stop-run switch. My mistake sorry for that.
grsthegreat
Generator Jedi Master
Generator Jedi Master
Posts: 1527
Joined: Mon Apr 20, 2020 5:59 pm

oh, sorry. the stop switch generally grounds out the spark going to the plug. im not too familiar with portable units as i service whole house units. there should be a grounded wire going to one side of the stop switch. if you interrupt that the unit should be able to start.
Bassguitarist1985
Contributor
Contributor
Posts: 53
Joined: Wed Jan 23, 2019 12:37 am

You sure its the switch? Check with ohm meter? Oil switch is time delayed so you would get spark for a few seconds before engine shuts down. Possible ignition coil issue too.
rvs57lin
New Member
New Member
Posts: 6
Joined: Mon Nov 22, 2021 10:41 am

Thank you for the tips. I really think its my stop-run switch. As the last time I run my generator it ran great and I run it for 2 hours. I will get to the gd on that switch and see if I can by pass it.

Thanks again

RV