cat/olympian 2 wire start to generac its 3 wire start

Automatic/Manual transfer switch repair, wiring & troubleshooting questions
Post Reply
caterpillar epg tech
New Member
New Member
Posts: 2
Joined: Mon Oct 11, 2021 8:59 pm

I have a two wire start signal on the olympian 25 kw. i has to complete a dc ground to start and be held to stay running. the new generac 200 amp single phase has three terminals. dc pos and ground and then a terminal 23 that takes a ground signal from a gen control to actuate the transfer relay. I was thinking of adding timed relays to allow for spooling up of gen and transfer back to utility before the gen is shut off. any ideas or possible kit from generac that may be available? thanks
VelvetFoot
Top Contributor
Top Contributor
Posts: 197
Joined: Tue Dec 29, 2020 6:02 pm

I am just a homeowner but this device sounds interesting:

https://pspproducts.wpengine.com/?p=1063
Birken Vogt
Generator Guru
Generator Guru
Posts: 529
Joined: Sun Nov 11, 2018 12:02 am

It sounds like you have a transfer switch for a standard 2-wire generator and you have replaced it with a new Generac generator?

The Generac generator can work with the existing 2-wire switch, if that is what you have.
VelvetFoot
Top Contributor
Top Contributor
Posts: 197
Joined: Tue Dec 29, 2020 6:02 pm

Reading it again, you're probably right.
caterpillar epg tech
New Member
New Member
Posts: 2
Joined: Mon Oct 11, 2021 8:59 pm

VelvetFoot wrote:
Tue Oct 12, 2021 10:20 am
I am just a homeowner but this device sounds interesting:

https://pspproducts.wpengine.com/?p=1063
Thanks to all who answered. I believe this is the ticket.