Search found 6 matches

by stevegen
Wed Oct 12, 2022 10:47 am
Forum: General Discussion
Topic: No MAC address or SSID sticker
Replies: 4
Views: 451

Re: No MAC address or SSID sticker

The Generac technician stopped out this morning to check out the no-start issue that you helped me to fix. At first he thought the same thing. That I needed to claim my module. Turns out the unit came with the module, the sticker wasn't attached though. First time he had ever seen that. He was able ...
by stevegen
Tue Oct 11, 2022 11:07 pm
Forum: General Discussion
Topic: No MAC address or SSID sticker
Replies: 4
Views: 451

No MAC address or SSID sticker

24kw Generac serial #3011905912 My new unit did not come with the sticker that lists the MAC address and SSID. I called Generac and they gave me the code to allow the generator to start. They said the MAC and SSID could not be found. In trying to setup the WiFi, I find that information is required. ...
by stevegen
Tue Oct 11, 2022 10:51 pm
Forum: Generac Air Cooled
Topic: Testing NG Regulator
Replies: 11
Views: 466

Re: Testing NG Regulator

Grsthegreat, thank you so much. I added a regulator and it starts fine. I had spoken with Generac twice and at no time was an additional regulator mentioned. The gas company and the county building department signed off on the installation with out the additional regulator. Again, my sincere thanks....
by stevegen
Tue Oct 11, 2022 12:44 am
Forum: Generac Air Cooled
Topic: Testing NG Regulator
Replies: 11
Views: 466

Re: Testing NG Regulator

Isn't there a regulator inside the Generac? Perhaps I was on the wrong test port. There are two ports, an upper and lower. The upper port was used for the measurement.
by stevegen
Mon Oct 10, 2022 11:31 pm
Forum: Generac Air Cooled
Topic: Testing NG Regulator
Replies: 11
Views: 466

Re: Testing NG Regulator

55 inch water column.
by stevegen
Mon Oct 10, 2022 6:50 pm
Forum: Generac Air Cooled
Topic: Testing NG Regulator
Replies: 11
Views: 466

Testing NG Regulator

NG, 25 feet of 1" black pipe then 3/4" flex.
G0072101
3011905912

Error code 1100.
Reading on the top regulator test port is about 55" in/water/column. The same as main gas line. Testing was done by a hired HVAC tech. I have multimeter and hand tools. Thanks.
Steve