Re: Synergy "unsolvable problem" Error 1062
If you're referring to Generac customer support, their number is 888-GENERAC
- Mon Mar 27, 2023 9:51 am
- Forum: Generac Air Cooled
- Topic: Generac 5254 standby generator will not start
- Replies: 36
- Views: 19187
Re: Generac 5254 standby generator will not start
Typically a buzzing/clicking is a sign of a bad battery or battery cable connection. How did you load test the battery?
The starter replacement is done blind on these units, but it's not terrible. The starter can be rotated up and out of the back without really removing anything.
The starter replacement is done blind on these units, but it's not terrible. The starter can be rotated up and out of the back without really removing anything.
- Sat Mar 25, 2023 3:57 pm
- Forum: Generac Air Cooled
- Topic: Generac 12 KW LP gas hard/no start
- Replies: 20
- Views: 4853
Re: Generac 12 KW LP gas hard/no start
Hello, My 044560 is doing the same thing. Compression test was 100 and 86 PSI (unable to find what the correct opperting compression should be). Last 100 hours used approximately 1 quart of oil (first time having this problem). Air filter has some oil in it. Fuel pressure at secondary port is 10.5"...
- Sat Mar 25, 2023 12:22 pm
- Forum: Generac Air Cooled
- Topic: 22kw G0070433 repeated charger warning light
- Replies: 5
- Views: 202
Re: 22kw G0070433 repeated charger warning light
Have you called a dealer out to have a look at it..?
- Fri Mar 24, 2023 5:02 pm
- Forum: Generac Air Cooled
- Topic: New 22kw won't start
- Replies: 4
- Views: 68
Re: New 22kw won't start
The Generac install manual doesn't pertain to high pressure fuel systems like your LP setup from the tank to the secondary reg.
- Fri Mar 24, 2023 5:02 pm
- Forum: Generac Liquid Cooled
- Topic: controller giving me a stop warning and error code
- Replies: 4
- Views: 77
Re: controller giving me a stop warning and error code
The Protector series use the 0H1827 style probe, but it's not connected to the 14 wire like the retro fit kits were (they need signal conditioner power).
- Fri Mar 24, 2023 5:01 pm
- Forum: Portable Generators
- Topic: Generac RS5500 - Micro switch in Power Dial
- Replies: 2
- Views: 30
Re: Generac RS5500 - Micro switch in Power Dial
I tried to find the part number you provided but it doesn't come up. Are you sure that's the correct part?
- Thu Mar 23, 2023 5:48 pm
- Forum: Generac Liquid Cooled
- Topic: controller giving me a stop warning and error code
- Replies: 4
- Views: 77
Re: controller giving me a stop warning and error code
Most times the probes are in the top tank of the radiator. If your radiator is full, it may mean that the probe is failing, might have buildup on it, or may be that a wire has come loose somewhere. It also may be that there is an air pocket working its way around and the level really is dropping (si...
- Thu Mar 23, 2023 5:43 pm
- Forum: Transfer Switches
- Topic: Any other causes of N1 & N2 fuse failures other than heaters?
- Replies: 7
- Views: 101
Re: Any other causes of N1 & N2 fuse failures other than heaters?
Anytime I see a loose push on connector, I take my wire strippers (which have little pliers on the end) and pinch the connector a bit. They don't ever fall off again!
- Thu Mar 23, 2023 8:39 am
- Forum: Generac Air Cooled
- Topic: generac starter motor kit 0e0601asrv plastic cap
- Replies: 2
- Views: 94
Re: generac starter motor kit 0e0601asrv plastic cap
It's just there to keep dirt/junk off the shaft and spring assembly. They do normally get left in place when installing the starter.