Re: Load Shed Module
If there are abnormalities in power quality with the grid it can affect these and shed. There have been some changes in the way they operate over the years.
- Sat Mar 11, 2023 7:52 pm
- Forum: Generac Air Cooled
- Topic: Overspeed error on 20kW Generac NG model 0058871
- Replies: 14
- Views: 2064
Re: Overspeed error on 20kW Generac NG model 0058871
I have one sitting the yard that was doing it too. You could swap controllers, steppers. I’ve seen it when one butterfly got sucked into the cylinder. This showed low compression on one cylinder and the customer said replace it. It was a nexus unit.
Start looking elsewhere, mechanical issues.
Start looking elsewhere, mechanical issues.
- Fri Mar 10, 2023 8:22 pm
- Forum: Generac Air Cooled
- Topic: 2008 8KW GH410 RPM Sense Loss
- Replies: 5
- Views: 252
Re: 2008 8KW GH410 RPM Sense Loss
A valve adjustment is worth doing especially if you don’t know when or if it’s been done recently. Do like he says and short across those terminals on the starter solenoid to see if it will turn over. These fail fairly regularly. Having a set of automotive jumper cables are handy to have too. If the...
- Tue Mar 07, 2023 5:15 pm
- Forum: Generac Air Cooled
- Topic: Which manual do I need?
- Replies: 8
- Views: 199
Re: Which manual do I need?
Valves and making sure the orifice is set to the correct fuel type. I find ones that have been hanging on for years not converted to propane. Exercising, running poorly, only getting by by the fact that there haven't been any serious outages or load on it.
- Sun Feb 26, 2023 7:22 pm
- Forum: Generac Air Cooled
- Topic: 22k air cooled - overcrank 1100 and Popping Sound When Starting
- Replies: 4
- Views: 234
Re: 22k air cooled - overcrank 1100 and Popping Sound When Starting
Valve adjustment. How many run hours? Then I’d look at coils. Will it run on one cylinder, trying both to see if it’s different. Lastly is the stepper moving the throttle as it’s supposed to?
- Sun Feb 26, 2023 4:22 pm
- Forum: Generac Air Cooled
- Topic: Copper tubing
- Replies: 2
- Views: 176
Re: Copper tubing
I think you'll find the reverse thread on at least the tank itself. POL is what it's called. The regulators come with various inlet and outlet sizes. POL or NPT inlets, and various outlet NPT sizes.
- Tue Feb 21, 2023 6:32 pm
- Forum: Generac Air Cooled
- Topic: Error code 1902 New Install
- Replies: 19
- Views: 536
Re: Error code 1902 New Install
Agreed, if the conductors aren't compromised, then probably some heat shrink sleeving and additional care arranging the wire during reassembly. Making sure there wasn't any likelyhood that this would happen again, vibration, etc.
- Mon Feb 20, 2023 8:03 pm
- Forum: Generac Air Cooled
- Topic: 7500E, .8 hours, won't start...
- Replies: 28
- Views: 462
Re: 7500E, .8 hours, won't start...
I think I heard that from a bunch of customers over the years. Just put some love to a Briggs portable last week, valve adjustment, carb, coil plug, oil change and air filter. Runs great now after all the stinky mouse mess was cleaned out and otherwise normal maintenance done. Please use it regularl...
- Mon Feb 20, 2023 6:06 pm
- Forum: Generac Air Cooled
- Topic: 7500E, .8 hours, won't start...
- Replies: 28
- Views: 462
Re: 7500E, .8 hours, won't start...
What I’ve found with these and any other portable, that if it isn’t used regularly, the carb gets gummed up. I don’t bother with rebuilding them, I just swap the carb out with new and implore customers to run them more often even if unloaded and shut down with the fuel shut off.
- Sun Feb 19, 2023 1:44 pm
- Forum: Generac Air Cooled
- Topic: Please Help! Generator starts and stops randomly outside of scheduled run.
- Replies: 3
- Views: 124
Re: Please Help! Generator starts and stops randomly outside of scheduled run.
The problem can lie ahead of the panel or transfer switch all the way out to the pole or transformer. Loose connections along the way back to the pole or transformer will do this. Get an electrician involved. The utility may have to be involved. Whoever shows up first will tell you whose responsibil...